I'm 1st AD on a two-day apartment shoot. No generator, no electrician, just the DP's kit and the flat's wall sockets. Building is old and the owner says breakers trip 'sometimes'. What should I make sure happens before anyone plugs in a light?
First map the circuits. Flip each breaker with a tester or a cheap lamp plugged in and label which sockets go dead. In older buildings one breaker often feeds two rooms. Then load math per circuit: watts = volts x amps. A 15 A circuit at 120 V is 1800 W; a 20 A one is 2400 W. Plan continuous loads at 80% of that. In a 230 V country a 16 A circuit is 3680 W, so about 2900 W planned. Use proper stingers sized for the load, never daisy-chained household strips. Run cable flat and tape or mat the crossings. Nobody opens the panel or tie-ins unless a licensed electrician does it. Source: CSATF, Safety Bulletin 23 and its addenda, https://csatf.org/toc_safety_bulletins
If you end up adding a small generator on day two, think of sound and safety together, because both care where it sits. Put it as far from the set as the cable allows and point the exhaust away from the building and any open window. CSATF has a separate addendum to Bulletin 23 on grounding portable generators. Read it before you rent one, because the rental desk won't walk you through it.
Mapped every circuit the evening before and taped the breaker numbers on the sockets. The DP split the kit across three circuits with a written load per circuit, the kettle went on its own socket in the kitchen, and nothing tripped in two days. The owner was impressed, which helps when we ask to come back for pickups. Next time I will book the electrician anyway.